Assembly to control 16 motors 115volt

Hello, I would like to control the start of 16 electric motors with a temperature sensor.

I wish I could adjust the temperature for starting the motor from my computer.

I saw controller type Phidgets 0/16/16, is this type of controller I need?

If so, can we control 2 card with the software?

my setup would look like more like this :wink:

WOW thank you for information ! :smiley:

I order one card 8/8/8 with relay board to start and make test.

Hi TEKnowLOGY,

We don’t think the Phidgets 0/16/16 will be sufficient for your needs.

Have you chosen your thermal sensors? Most of them produce analog signals, which you wouldn’t be able to read with the 0/16/16 because it doesn’t have any analog inputs. The 8/8/8 model has 8 analog inputs.

Also, have you chosen motor controllers (or relays) to control your motors? Do you need to adjust the speed, or just turn them on/off? If you just want on/off, you can use the Elexol 8-Channel Serial Relay Module to control 115 VAC motors up to 5A each, and this module can be controlled by the 8/8/8.

If you want to control the speed, the solution requires more complex motor controllers (we don’t carry controllers for 115 VAC), but you will also need to verify if the 8/8/8 can generate compatible signals (depends on controllers selected).

What’s the nature of your project? Are you building a HVAC – heating, ventilation, air conditioning – system? If so, we don’t expect that the 5A limit of the relay module will be sufficient either…

Cheers,
Jeffrey

Hi TEKnowLOGY,

You would need one 8/8/8 board for each 8-relay module, but you would need two boards anyways if you still wanted to read 16 temperature sensors (such as RB-Phi-68): 8 temperature sensor per board.

Do you know what is the current consumption of the ventilation motors? It’s important that it’s verified because it’s possible it exceeds 5 amps, in which case the Elexol 8-Channel Serial Relay Module won’t be sufficient for your needs.

Regards,
Jeffrey

température control is : RB-Phi-68

motor : just ON and OFF

Is it posssible to control 2 card ‘’ Elexol 8-Channel Serial Relay Module ‘’ with ‘’ 8/8/8 model ‘’ ? in same time

my setup is for ventilation in a motel room :slight_smile: